Issue
Lost all Xenta Server trendlog values in TAC Vista
Environment
- Vista Workstation
- Xenta Server
- Xenta 511, 527, 701, 711, 721, 731, 913
Cause
Changing a folder name in XBuilder and updating TAC Vista.
Resolution
If you change a folder name in XBuilder and update TAC Vista, all trendlogs in this folder will be recreated and will have to be started again. This also means that you will lose all the log data.