Lock path of binding point does not work

Lock path of binding point does not work

Issue

When trying to lock the path of a binding point, the path doesn't change.

Right clicking on a binding path to lock the pathRight clicking on a binding path to lock the path

The locked symbol appears (1), but nothing happens to the path (2).

1. The path is unchanged. 2. The lock symbol is displayed1. The path is unchanged. 2. The lock symbol is displayed

When trying to save the changes the locked symbol (1) disappears.

Product Line

EcoStruxure Building Operation

Environment

Building Operation Workstation v. 3.0

Cause

Lock Path is not converting the relative path to an absolute path hence the save is not working as expected. This works fine in version 2.0 and is fixed in version 3.1.

Resolution

  1. Upgrade to version 3.1 where this problem is fixed.
  2. In version 3.0 the path can be manually updated to the correct locked path before saving.
    Manually updated binding path to a correct locked pathManually updated binding path to a correct locked path
    In the example above the path to the Analog Value in the binding point is 
    /Server 1/test/Analog Value
    Therefore the correct locked path should be
    ~/test/Analog Value/Value
    Make sure you have locked the path before saving.