Listview dump files for monitoring and BACnet offline problems

Listview dump files for monitoring and BACnet offline problems

Issue

Useful listview dump files for checking and monitoring systems, including BACnet find and offline problems

Product Line

Andover Continuum

Environment

  • Listviews
  • BACnet check
  • Alarm Events, Access Events Error Events
  • COV increment check

Cause

Useful listviews for monitoring and debugging a Continuum site

Resolution

Useful Listview dump files

Once the .dmp file is imported in to Continuum, the listviews will be found at the top of the Listview files on the root.
Run the listview and the go to "Object/Export to a .CSV file if a copy of the results is required.

The BACnet Check devices listview is helpful if "find New BACnet" device fails to find the device. The device may have been previously discovered on a different network and not deleted correctly.
Also, duplicated BACnet devices can be checked, this can cause majors problems with controllers going offline and flooding various networks with data.