Links or binding paths In TGML graphics are changed after the graphic is edited

Links or binding paths In TGML graphics are changed after the graphic is edited

Issue

A site is converted from TAC Vista to EcoStruxure Building Operation using TAC Vista Conversion Tool and all TGML graphics work fine.

After a TGML graphic is edited all links or binding paths in the graphic are changed.
Example:
Before
Before.png

After
After.png

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Workstation
  • TAC Vista Conversion Tool version 2.X

Cause

This issue will only be seen in TGML graphics which originally have been OGC graphics in TAC Vista and then converted to TGML graphics at some point.

Resolution

This issue is fixed in TAC Vista Conversion Tool version 3.02 and later.

Redo the conversion using a version of the TAC Vista Conversion Tool 3.02 or later. 