Is the SE7000 series controllers with LonWorks communications compatible with TP/FT -10 channels?

Announcements

Is the SE7000 series controllers with LonWorks communications compatible with TP/FT -10 channels?

Issue

Is the SE7000 series controllers with LonWorks communications compatible with TP/FT -10 channels? 

Environment

SE7000 series controllers

Cause

The datasheet indicate network compatibility with Echelon LonTalk but there is no mention of the compatibility with TP/FT-10 channels / networks. This may be unclear to some. 

Resolution

The SE7000 series is compatible with LonWorks TP/FT-10 channels. Refer to the datasheet for 14240R which is the free topology transceiver used in the SE7000

capacitors, LPT-10 Link Power Transceivers
Free Topology Transceivers, and, with suitable DC blocking
capacitors, LPT-10 Link Power Transceivers
FT 3120 / 3150 s mart Transceivers, FTT-10 and/or FTT-10A
Free Topology Transceivers, and, with suitable DC blocking
capacitors, LPT-10 Link Power Transceivers