Installing Webclient over the top of Cyberstation

Installing Webclient over the top of Cyberstation

Issue

If only Cyberstation was installed, but Webclient is needed will installing Webclient over the top work?

Product Line

Andover Continuum

Environment

  • Webclient
  • Windows XP
  • Windows 7
  • Windows Server 2003
  • Windows Server 2008

Cause

At times a Webclient install is needed but a Cyberstation installation was done.

Resolution

Trying to install over the top will not install the needed web components. The recommended installation of Webclient when Cyberstation has been installed first is as follows:

  1. Uninstall Cyberstation
  2. Reboot
  3. Install Webclient
  4. Run the following command after the install to re-register .NET framework with IIS.
    C:\Windows\Microsoft.NET\Framework\v2.0.50727\aspnet_regiis.exe -i​