I/NET compatibility with EcoStruxure Building Operation 3.0.1 and higher

I/NET compatibility with EcoStruxure Building Operation 3.0.1 and higher

Issue

Upgrading from EBO 2.0.x to 3.0.x causes I/NET to become incompatible.

Product Line

TAC I/NET
EcoStruxure Building Operation Automation Server
EcoStruxure Building Operation Enterprise Serve

Environment

  • EcoStruxure Building Operation (version 3.0.1 and later)
  • I/NET Seven Software (All Versions)

Cause

I/NET Seven Software is built using a 32-bit interface. Starting with EBO 3.0.1, EcoStruxure requires the use of a 64-bit interface.

Resolution

For INET seven to operate with EcoStruxure Building Operation 3.0.1 it is necessary to
obtain a 64-bit DLL from the Exchange and install in the INET installation prior to the
upgrade.

  1. Search for INET IPortAPI64 - Software on Exchange. 
  2. Download the IPortAPI64_EBO.dll.
  3. Unzip the DLL and copy the DLL to the same folder as the 32bit INET install, by default this will be C:\Program Files (x86)\INET Seven folder.
    • Note: if INET was installed in a different folder this can be found by examining the
      Windows registry key ”INETSevenPath” at HKLM\SOFTWARE\WOW6432Node\CSI -
      Control Systems International\I/Net 2000/Configurations.
  4. Install EcoStruxure Building Operation 3.0.1
  5. When the ES restarts the InetPlugIn will connect to InetIoSrv via the 64-bit IPortAPI64_EBO.dll.