Issue
I/A Series (Niagara) R2 station, needs a LON shadow object for a Square D Altivar 21 with Program ID 80:00:13:3C:0A:0A:04:50. The closest match is Atv21, with Program ID 80:00:13:3C:0A:0A:30.
Environment
I/A Series (Niagara) R2 station in a UNC with a LON trunk, build 532, 529, or 522
Square D drive, Altivar 212, with LON card, Program ID 80:00:13:3C:0A:0A:04:50.
Cause
Square D Altivar 212 with a new LON profile and XIF file, program ID 80:00:13:3C:0A:0A:04:50
Resolution
Download a new jar file: lonSquareD-2.303.532a.zip, which includes a shadow object named Atv212, manufacturer Id = TA_Control, and Program ID = 80:00:13:3C:0A:0A:04:50.
LonUtilities Manager after the jar file has been installed: