Issue
How to extract the status of DI 01 from a Viconics thermostat for plotting on a web graphic in Niagara.
Environment
Niagara R2
Cause
Integration requirement
Resolution
In the Se76PIR shadow object, use nvoSccStatus, bit 18 (see illustration below).
Link to a DynamicDemux object (located in the lonworks jar file, conversion folder) to gain access to bit 18. Now it can be used in the Niagara station for graphics or logic programming.