Issue
How to use door alarm to trigger buzzer, including "Door Open Too Long" or "Door Forced"?
Environment
I/NET
Cause
This is a normal application for access control system, which is needed for some customers.
Resolution
The following steps need to be followed:
-
Set Event Definition for the strike point. Choose the Event type to "Door Open Too Long" or "Door Forced". If the buzzer needs to be reset automatically after alarm disappears, another sequence should be triggered by “Door Normal” event.
-
Define the Event Sequence to trigger buzzer point.
After setting, when there is door alarm, the buzzer will be triggered.