Issue

How to Take a Controller to boot from the I/NET Host workstation

Environment

I/NET

PCU DCU

Cause

Performing a station restore or bin file restore fails.

Resolution

  1. In I/NET Select Edit>Host Computer>Software Restore
  2. Select the Controller you wish to take to boot
  3. Select the checkbox marked "Software"
  4. Click OK
  5. When the software download reaches 10% of the total size click Cancel
  6. You can verify the controller is in boot by attempting to connect to it, or by using netcon
  7. Repeat steps 1-4 to allow the bin file to completely load before using the controller
  8. Make sure you do a station restore to the controller after the "Boot" process