How do you locate a list of error numbers and reasons in Cyberstation?

Issue

At times numbered errors pop up in Cyberstation or you may see a numbered error in the Error Listview

Product Line

Andover Continuum

Environment

  • Continuum Cyberstation
  • Windows

Cause

Numbered errors appear in Cyberstation or in an Error Listview and an explanation is needed for troubleshooting

Resolution

With Continuum running and with the focus on the main Continuum screen or Continuum Explorer, press F1 to bring up the help menu

  1. Select index
  2. Type in ‘error’
  3. Select Error Messages, Cyberstation
  4. This displays a list of some of the error messages that may come up in Cyberstation.

This is not a comprehensive list and it doesn’t provide solutions, but gives an initial idea of what is happening for troubleshooting.