Issue
How can I see more than three property windows when programming a controller with VisiSat.
Environment
- VisiSat
- MN50 Series controllers
Cause
The default amount of property windows allowed is set to 3. This can be changed if required in the “settings.ini” file for the project.
Resolution
Default = "Number of Property Forms=3"
Changing this to "Number of Property Forms=9" allows you to have 9 property windows.