Issue

The Heat Meter now has a barcode where the customer number use to be printed. From the customer number the modbus slave ID could be determined.

Product Line

Field Devices

Environment

  • Modbus
  • Heat Meter

Cause

The Heat Meter now has a barcode where the customer number previously had been printed. From the customer number the modbus slave ID could be determined.

Resolution

The customer number is a replica of the serial number. The last 3 digits are the modbus slave ID, except when the last 3 digits are 248 or higher, then the slave ID is the last 2 digits.

In this case, the slave ID is 210.