Issue
Site upgrading ES from 3.2.1.630 to 3.2.3.59. After the upgrade, some graphics and custom types are missing
- Before Upgrade: EBO 3.2.1.630
- After upgrading to EBO 3.2.3.59
Product Line
EcoStruxure Building Operation
Environment
- Building Operation Workstation
- Building Operation Enterprise Server
Cause
Error "is not defined in the target version, discarding object ~ " is found in the upgrade log.
Resolution
- There are known issues when upgrading incorrectly, i.e. from the same major. minor (3.2.1.630) to the same major. minor(3.2.3.59) since the work and original folders are the same.
- Thus, When updating (not upgrading) within the same version (from 3.2.1 to 3.2.3) we must use a hotfix. We shouldn’t be using a Full installer.
- In this case, Installing the latest (Consolidation point hotfix 3.2.3.1300) resolved the issue.