Getting an error when adding the ASD service to a Niagara R2 station

Getting an error when adding the ASD service to a Niagara R2 station

Issue

Getting an error when adding the ASD service to a Niagara R2 station

Environment

  • Niagara R2
  • ibsAsd driver

Cause

The error indicates that the serialDriver jar file has not been installed.

Resolution

The ibsAsd driver will not function without the serialDriver jar file. The serialDriver includes communications class files needed to support ibsAsd.

To correct the issue, use the Installation Wizard in the admin tool to install the serialDriver jar.

Caution: The station must have the Serial Driver installed. It is recommended that the 516b version released in July 2006 be used. The jar files as well as the ASD driver documentation (F-27429) are available for download from The Exchange Download Center