Issue
Is there an easier way to get log information out of a Niagara R2 Enterprise Server station other than by using a web browser, saving the data, and importing it to Excel?
Product Line
TAC IA Series
Environment
I/A Series R2 (Niagara) station with logs.
Cause
Tech tip.
Resolution
There is no easier way to get log information than to use a web browser, save the data, and import to Excel. However, by default, a query to the archived log limits the number of records to 2500. This limit can be changed by adding $limit=xxxx.
Note: Attempting to query a large number of records (> 7500) may cause the process to fail due to timeouts.
A review of the cloudscape2excel document provides some details.