43549members
218144posts

General recommendations for LonWorks system architecture

General recommendations for LonWorks system architecture

Issue

What are the general recommendations for LonWorks system architecture?

Product Line

TAC Vista, TAC IA Series

Environment

  • LNS database
  • LonWorks network
  • Vista Server
  • I/A Series MNL

Cause

Understanding the different communication speeds and optimal site design can lead to improved performance of LON traffic on a network.

Resolution

There are three levels supported by LonWorks.

  1. TCP/IP
  2. 1.25mbs high speed backbone
  3. 78Kbs FTT-10 level

Our recommendation is to maximize the use of TCP/IP, minimize the use of the 1.25mbs high-speed backbone and use a tiered structure of 78Kbs LON segments. The IP provides high-speed data transfer, which is good. The 1.25mbs high-speed bus works fine, but it has a number of special requirements that must be adhered to for proper operation. The flexibility of this 1.25mbs network is limited for the expansion of new Lonworks segments, whereas the TCP/IP is more in line with current building infrastructure making it easier to expand the LonWorks system.

In the TCP/IP there are two options that allow for better communications.

  1. Standard TCP/IP configuration that will work well for most middle-sized networks. This is standard with NL220 or Lonmaker installations
  2. Orion Stack is an improvement on the standard TCP/IP and can poll multiple values at one time helping improve the TCP/IP response on large networks. More information in setting up an Orion stack improved TCP/IP LonWorks network.
Tags (2)
Labels (1)
No ratings