Issue
Finding a new BACNet device causes a BCX controller to show in the Continuum Explorer with the icon of a Workstation
Environment
- BCX
- Continuum Explorer
- CyberStation
Cause
There are incompatible revisions between the controller and the CyberStation.
Resolution
- Delete the BCX from the BACNet view
- Choose one of the following options:
- Upgrade the CyberStation to version 1.73 and higher
- Downgrade the BCX below revision 4.4.
Review the Compatibility matrix posted on the Buildings Business Extranet for compatible revisions of products.