Filtering Trend Log entries to be shown in a Notification Report

Filtering Trend Log entries to be shown in a Notification Report

Issue

Unable to configure Notification Report Template to filter the entries from a trend log that will be shown in the report

Product Line

EcoStruxure Building Operation

Environment

Building Operation Enterprise Server

Cause

In many cases it is desirable to show a sub-set of entries from the trend log included in a report filtered by a criteria such as date range  

Resolution

As of EBO version 3.1 the only way to specify a sub set of entries is via the 'Number of records' property

NotifRprtTemplateConfig.png

Starting in version 3.2x, the Notification Report Template configuration will allow filtering by custom date as well as providing the following built in filters

Today

Yesterday

This week

Last week

This month

Last month

This year

Last year