42268members
186166posts

Failed to call pILiveData error when editing Schedule object in Continuum 1.94

Failed to call pILiveData error when editing Schedule object in Continuum 1.94

Issue

After upgrading to Continuum 1.94, Cyberstation throws the following error:

Failed to call pILiveData -> GetLiveData().  ACDataServices has an error.

Product Line

Andover Continuum

Environment

  • Continuum 1.94
  • Schedule
  • Error

Cause

This behaviour is due to a bug that was described in TPA-BOST-12-0002 00 Schedule Exception Errors.

Resolution

Install the CyberStation v1.94 SP1 - Software which can be found on the Exchange Extranet.

Tags (1)
Labels (1)
No ratings