41451members
184468posts

External resistors required for Biasing and Terminating RS-485 trunks connected to an Automation Server

External resistors required for Biasing and Terminating RS-485 trunks connected to an Automation Server

Issue

External resistors are required for Biasing and Terminating RS-485 trunks connected to an Automation Server (AS)

Product Line

EcoStruxure Building Operation

Environment

  • SmartStruxure Automation Server (AS) with  RS-485 trunk(s) under it.
  • Field controllers on the RS-485 trunk; for example, the Network 8000 ASD controllers (MZ2, PEM1, etc) 

Cause

Bias and terminating resistors are not built into the AS hardware.

Resolution

External resistors are required for Biasing and Terminating RS-485 trunks connected to an  Automation Server (AS).

See the Technical Reference Guide, revision 1.3, pages 2723, 2724, and 2771.

 

Also check out the SmartStruxure-RS485-Network Installation Quick-Help video on the Exchange.

Tags (5)
Labels (1)
No ratings