Error "Setting NeuronID of router" when upgrading a Lonmaker Database to NL220

Issue

When browsing to the LNS database on the new NL220 project screen, an error message says, "Setting NeuronID of router <%s> ..._O"

Product Line

Other, TAC Vista

Environment

  • Lonmaker
  • Newron NL220

Cause

The name of the database folder is over 12 characters. For example, C:\LM\Db\367_Collins_St

Resolution

To correct this error, rename the folder containing the lonworks database to 12 characters or less.

The above example folder name in the Cause heading could be renamed to  C:\LM\Db\367CollinsSt