Issue
When launching Continuum the following error window comes up
The main menu splash is not displayed and the application randomly crashes with an MFC error.
The following Application error is seen in the windows log.
Continuum.exe
1.94.0.1
4f735b82
MFC80.DLL
8.0.50727.6195
4dcdeca2
c0000005
00023b10
f94
01ce6c36e741312b
C:\Program Files (x86)\Continuum\Continuum.exe
C:\Windows\WinSxS\x86_microsoft.vc80.mfc_1fc8b3b9a1e18e3b_8.0.50727.6195_none_cbf5e994470a1a8f\MFC80.DLL
295d2fa7-d82a-11e2-9a81-00188b6cfffd
Environment
CyberStation
Cause
Corrupted Continuum.MNU menu file.
Resolution
Remove the corrupted menu file and replace with a good file from another WS.
Note:
When copying a menu file from another WS make sure it is the same type in terms of 32 versus 64 bit as there are paths in the file that differ depending on the OS type.