Issue
Error: Subsystem NS, #149 lcaErrNsConflictWithCurrentNetwork
This error will be generated if you open a network that is already opened using a different network interface, LNS type, or database directory.
Environment
LonMaker
NL220
Vista
LNS
Cause
After restoring a LonMaker database, or upgrading a LonMaker system, each LNS database has to be opened before the Vista server is started or you get this error. Same as with LonMaker, if you start the NL220 stand alone, and then start Vista, the LNS server will not be conflicted.
If switching between LonWorks Interface types (example: RNI to PCLTA) you may receive this error when trying to open the LonMaker drawing.
Cannot run LNS Database Validation Tool with the database open (Start > Programs > Echelon LNS Utilities > LNS Database Validation Tool 3.2).
Resolution
-
Shut down the Vista Server.
- If Vista Server is set to run as a service (Control Panel > Administrative Tools > Services > TACOS) manually stop the service.
- Open each LNS database network attached and onnet.
- Restart the server.
If this error occurred from switching LonWorks Interface types, rebooting the PC should clear the error.