Error Message: No text, Red Hand Only

Error Message: No text, Red Hand Only

Issue

When Starting I/NET you get a blank error message with a Red Hand.

Environment

I/NET

Remote Client Configuration

Cause

You are getting the Red Hand error because the active configuration is a Remote Client Configuration and the primary Server cannot be reached or the Network is down.

The Red Hand may also appear when I/NET cannot connect to the currently configure SQL database

Resolution

Option 1 -

  1. Check that you are connected to the network.
  2. Ensure that the Server you are remoted into is started and online

Option 2-

  1. Open I/NET Configuration
  2. Change the Active Profile to one that is Standalone