Issue
Editing TAC Xenta 280/300/401 that has the same XIF file
Environment
- Xenta Programmable Controllers
- Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B
- Menta
- NL220, LonMaker
Cause
The second method can cause a total mess in the LNS database regarding which Device Template the different devices then will belong to.
Resolution
Tested both with LonMaker and NL220.
If you have several Xenta280/300/400 that has the same XIF file (which is a not an unusual scenario), and you want to edit a few of the MTA files, maybe regarding the SNVTs, then it is recommended to:
- Edit Device A, Download app and params Device A
- Edit Device B, Download app and params Device B
- Edit Device C, Download app and params Device C
- etc
and NOT:
- Edit Device A
- Edit Device B
- Edit Device C
- Download app and params Device A
- Download app and params Device B
- Download app and params Device C