Issue
Updating a application specific controller with a later firmware version
Environment
NL220
Cause
Enhancements in firmware version need to be implemented into existing controllers of older firmware versions
Resolution
Here are the steps to download a new APB or NXE file in NL220.
- Locate the controller you wish to update in NL220. Right mouse click and select "Copy configuration values to memory"
- Right click on the same controller and select "Download Program"
- Browse to the new APB or NXE file you want to download
- Once the download is complete you can paste the configuration back into the controller. Right click on the controller again and select "Paste configuration value(s) from memory"
The controller is now updated with the new application.