Issue
- Downloading a 7793 save file to a 7798 Controller
- Running into a problem when trying to download a 7793 save file to a 7798 Controller
- Keep getting an error when it tries to download the I/O Configuration
Product Line
TAC INET
Environment
- I/NET Seven
- 7793
- 7798
Cause
The I/O Configuration for both of these controllers is different. The 7793 Controller is a dual station device while the 7798 Controller is a single station.
Resolution
In order to fix this, contact Product Support. We will provide you with the time required to convert these files and a Price Quote for the work involved.