Doors and Reader Expanders not transitioning from Continuum database to Security Expert

Doors and Reader Expanders not transitioning from Continuum database to Security Expert

Issue

The Continuum Database Transition Tool does not transition the doors even though they are present in the Continuum database being transitioned  

Product Line

Security Expert

Environment

Security Expert Server

Cause

Incorrect configuration of the Continuum Transition Tool

Resolution

In the 'Record Types' tab of the Continuum Transition Tool, there is a checkbox labeled 'Include Anti passback Programming' If the doors on the Continuum system are configured for anti-pass-back then the checkbox has to be ticked to match the Continuum configuration of the doors.

TransitionToolIncludeAntiPassbackProgramming.png