Displaying Correct Regional Units in Webstation

Issue

Metric vs. Imperial Units as displayed Using Webstation Regional Settings

Any device, will by default, show configured units. Regional settings must be applied to normalize all devices.

Product Line

EcoStruxure Building Operation

Environment

  • Webstation
  • TGML Graphics
  • SNVT values

Cause

Incorrect Units will appear in webstation if webstation regional settings are not configured correctly.

Resolution

  1. Log into Webstation
  2. Select Settings > Change Regional Settings



     
  3. Select the desired Language
  4. Select the desired Measurement system
  5. Click Ok

NOTE: Settings are preserved via a cookie stored on the local PC. Any time cookies are deleted this will return to its default setting.