Direct Connect to Xenta 527-NPR

Direct Connect to Xenta 527-NPR

Issue

Direct Connect to Xenta 527-NPR

Product Line

TAC INET

Environment

  • I/NET
  • Xenta 527
  • Xenta 527-NPR

Cause

Newer versions of Xenta 527-NPR with 5.1.0 and 5.1.1 revisions are unable to be directly connected to the system.

Resolution

  1. Using the FTP connection through IE (Internet Explorer) to connect to the device.
  2. Log on using the root username and password
  3. Now go to sys/system/hwconfig.cfg
  4. Copy out the hwconfig.cfg file and open it with Notepad
  5. Modify the part that says serial_A_function="7" and change it to "5"
  6. Save this and now copy it back in again.
  7. Restart the device
  8. Start I/NET and the direct connect through the NPR to the system should be working now.

Warning: Reloading the system program (such as performing upgrades) will remove this change.