Default Device ID / Device Instance of SE7000 series BACnet controllers

Default Device ID / Device Instance of SE7000 series BACnet controllers

Issue

Without knowing the Device ID / Device Instance these devices cannot add to the MSTP network in the AS or ES.

Product Line

Andover Continuum, EcoStruxure Building Expert, EcoStruxure Building Operation, Field Devices

Environment

  • Automation Server
  • Enterprise Server
  • BACnet
  • SE7000

Cause

Only the MAC ID / Com Address is shown in the display but not the Device ID / Device Instance.

Resolution

SE7200x Models

Default Device ID is set to: 72000 + MAC

  • Where MAC is the current MAC address of the device.

The device ID will also be upgraded as soon as there is a change to the device’s MAC.

For example, when a SE7200F5045B controller with a MAC address of 41 is connected to a network, its default Device Name will be SE7200F5x45B-41 and its default Device ID will be 72041.

SE73xxx Models

Default Device ID is set to: 73000 + MAC

  • Where MAC is the current MAC address of the device.

The device ID will also be upgraded as soon as there is a change to the device’s MAC.

For example, when a SE7300C5045B controller with a MAC address of 63 is connected to a network, its default Device Name will be SE7300C5x45B-63 and its default Device ID will be 73063.

Click here for the Integration Manual.

Please refer to the SE7300 series BACnet controller does not come online in StruxureWare Building Operation if SE7300 controller does not come online.