Issue
Creating a new cardholder in webClient gives the error 'Response XML String is Corrupt'
Environment
webClient
Cause
A modification must be made to the ServerUtils.aspx file.
Resolution
- Have all users log out of webclient
- On the webclient machine, go to c:\program files\webserver folder, make a copy of ServerUtils.aspx.
-
Edit the existing copy of ServerUtils.aspx and add the following text to the first line. validateRequest='false'
Note: There are brackets < >at each end of the following lines in the ServerUtils.aspx file
Original line: %@ page language="c#" inherits="WebClient.ServerUtils, App_Web_w0emuixz" %
Edited line: %@ page language="c#" inherits="WebClient.ServerUtils, App_Web_w0emuixz" validateRequest='false' %
- Close Internet Explorer if it was open
- Log back into webclient and then create a new cardholder and no error will show.