Creating Critical, Priority, Routine, Transaction event pages on a 527/731

Issue

Creating Critical, Priority, Routine, Transaction event pages on a 527/731

Environment

  • Xenta Server
  • Xenta 527, 731

Cause

When using Vista to access an I/NET network you have 4 views for the Alarms and transactions. To create these views on the web with a Xenta 527 or Xenta 731 you will need to create event pages with different filters.

Resolution

  1. Add a new event page in Xbuilder and use the InetAMT filter file.
  2. Right click on the event page and select Setup Event Viewer.
  3. Click the filter icon in the top left corner and use the following guidelines for the type of page you are trying to create:
    Critical Alarms - Priority From 1 To 1
    Priority Alarms - Priority From 2 To 2
    Routine Alarms - Priority From 3 To 3
    Transactions - Tenant: *
  4. Each event page will have a different filter. To match I/NET or Vista you will need to create four pages.