Could not open the specified Application Device load image (*.APB) file. (Subsystem: LNS, #10)

Issue

The Object Server is attempting to open a file that is already opened by another application.

Error: LNS #10 lcaErrFileOpen Lca : Could not open the specified Application Device load image (*.APB) file. (Subsystem: LNS, #10)

Product Line

TAC Vista

Environment

  • NL220
  • Vista
  • LNS

Cause

Trying to load an application image to a Xenta 102-AX from NL220 by selecting the default APB extension may generate this error.

Resolution

Use the .NXE rather than the .ABP.