Copying graphics with I/NET Tool Icons and Symbols Icons from one PC to another PC, causes the path from the Icons to unlink.

Copying graphics with I/NET Tool Icons and Symbols Icons from one PC to another PC, causes the path from the Icons to unlink.

Issue

I added some I/NET Tool Icons and Symbol Icons to a graphic page on one PC. Then copied the Graphic page to another PC and the link from these Icons are gone. What is wrong?

Environment

I/NET Seven Site using Graphics

Cause

I/NET tools Icons and Symbol Icons on Graphic pages does not save the link from one PC to the next

Resolution

The I/NET tools Icons and Symbol Icons on a Graphic pages does not save the link from one PC to the next.

  1. Copy the graphic page to the customer's PC.
  2. Copy any Custom Symbol to the customer's PC
  3. Then edit each of the Icons and re-connect the links.