Issue
Using the Pocket Terminal 32 utility to set the UNC532 default gateway via the command GW 10.130.10.253 and then set the node configuration using the SDCU. Communications from the Sigma server to the controller failed. On checking the default gateway it had changed to 10.130.10.240.
Environment
Sigma (All versions)
SDCU
PocketTerminal32
Cause
Using SDCU to write the controller node configuration wrongly changes the previously set default gateway IP address.
Resolution
Configure the controller first using SDCU and then set the default gateway IP address using Pocket Terminal 32. Similarly, if any changes are made by SDCU then the default gateway IP address must be re-entered.