Continuum Access Control power supplies and enclosures

Issue

Access Control power supplies in UK are not available globally.

Product Line

Andover Continuum

Environment

  • Continuum ACX57 CX9702 PSU Power supply
  • Continuum enclosures

Cause

Power supplies for access control systems (for powering of door locks/maglocks etc) should be purchased locally.

Resolution

All of the globally available enclosures are detailed in the Enclosure Family Datasheet. This includes ones suitable for Netcontrollers, ACX's, bCX's, i2 and VAV controllers.

Power supplies for access control systems (for powering of door locks/maglocks etc) should be purchased locally to suit the site applications.

Product Support Services does not keep records of the equipment that may have been purchased locally. e.g. in the UK a company called Dantech is used for Enclosures and power supplies, please contact them directly if PSU connection details are required.
Dantech electronic engineering
3 Galliford Road Industrial Estate
Heybridge
Maldon
Essex
CM9 4XD
Tel: +44(0)1621856850
NOTE: The Dantech PSUs often include FR contacts (Fire Relay) that need to be powered by 12Vdc to enable the supply.