Connecting an I/NET SubLAN to a Security Expert SP-C

Connecting an I/NET SubLAN to a Security Expert SP-C

Issue

  • You are transitioning an I/NET security system to Security Expert
  • The I/NET subLAN must be moved from a 779x controller over to an SP-C

Product Line

Security Expert, TAC INET

Environment

  • I/NET Controller (779x)
  • Security Expert Controller (SP-C)

Cause

As you transition an I/NET system to Security Expert, you will reach a point where you are ready to start moving your I/NET subLANs over to SP-Cs.

Resolution

Use the following instructions to connect an I/NET subLAN cable to a Security Expert SP-C.

  1. At the I/NET 779x controller, disconnect the subLAN cable.
  2. At an SP-C, connect the subLAN cable as follows:      
    1. Attach the positive (+) wire to Reader Port 1 pin "D0".      
    2. Attach the negative (-) wire to Reader Port 1 pin "D1".

                      SubLAN-SPC-2.png

  1. If you wish to establish a closed-loop subLAN configuration, connect the other end of the subLAN wires to SP-C Reader Port 2 in exactly that same manner as you did at Reader Port 1.