Configuration of Sigma Live Alarm Printer Filtering

Configuration of Sigma Live Alarm Printer Filtering

Issue

How to correctly configure the Live Alarm Printer filtering in Sigma

Product Line

Satchwell Sigma

Environment

Sigma release 4.05 SP1, SP2 and SEB

Cause

General configuration advice

Resolution

The Sigma Live Alarm Printer filters provide the option of which alarms to print, and which to print immediately. It is only possible to select one filter, per function per printer.

  1. In the Sigma Alarm Manager select the "Configure" option, and then select "Printer Filters"
  2. Create a maximum of two printer filters, one to "Filter Alarms to Printer" and the second to "Filter Alarms to print now". In reality only one filter might be necessary, but this will depend on site printing requirements.
  3. In the Sigma Alarm Manager select the "Configure" option, and then select "Live Printers"
  4. Select a "Live Alarm Printer" from printer list.
  5. Select a filter in the "Filter Alarms to Printer" option.
  6. Select a filter in the "Filter Alarms to print now" option.
  7. This is the configuration completed for this printer.

If another printer is also required to print "Live Alarms" then repeat the above process again, making sure that the printer is highlighted first.