Changing the host server of a SmartX Controller

Changing the host server of a SmartX Controller

Issue

While moving a SmartX Controller from one AS-P to another, there is an error stating "The following devices appear to be hosted by another server. In order to host them, you must first right click the device and select 'Clear host information' ".

 

2019-10-31_10-29-02.png

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Automation Server
  • Building Operation Multi-purpose Controller
  • Building Operation Multi-purpose VAV
  • Building Operation IP-IO
  • Building Operation Room Controller

Cause

SmartX controllers can only be hosted by one automation server at a time.

Resolution

  1. Use the Device Discovery tab in the AS-P
  2. Once the MP is found, right-click on the device
  3. Select clear host information

2019-10-31_10-33-45.png

 

 