Issue
A Security Expert reader that supports Wiegand and RS-485 is wired for Wiegand. It is not working. It only works on RS-485.
Product Line
Security Expert
Environment
Security Expert Smart Card Readers which support both 125Khz and 13.56Mhz.
Cause
Tried to use a Smart Card Reader wired for Wiegand after it had been connected by RS-485 to the controller.
Resolution
Once a Security Expert Smart Reader is used in an RS-485 configuration it can only be used in a Wiegand configuration after being re-programmed with a configuration card designed for that purpose. The configuration card must be purchased through Schneider Electric.
This is because RS-485 is a two-way communication, intelligent wiring protocol. Once the reader is set in this two-way communication mode there is currently no way, without the configuration card, to go back to a less intelligent one-way mode like Wiegand.
Note: Readers manufactured in 2017 or before may have a firmware version that uses a configuration mode that will not respond to a configuration card. If you contact Schneider Electric for a configuration card, supply the serial number (SN) from the back of the reader on your request.