Issue
When attempting to edit a graphic on an SBO/EBO ES or AS the Graphics Editor reports it has lost connection.
Product Line
EcoStruxure Building Operation
Environment
Graphics Editor
Cause
A second instance of the workstation is running on the same computer
The firewall is blocking the connection.
The password was recently changed during the same session
Resolution
Solution 1
If you use Remote Desktop (RDP) to access the SBO/EBO ES remotely, a second instance of the workstation could be initiated.
Close the workstation on both the remote connection and at the SBO/EBO ES.
Then open the workstation either at the SBO/EBO ES or via remote connection, not both.
Solution 2
Check if the firewall has been enabled while logged in to the SBO/EBO ES or AS, and disable the firewall
Here is an example for McAfee
Solution 3
Make sure the network information (such as gateway) for the PC is entered correctly.
Solution 4
If you just changed the password of the logged in user, log out and in again
Solution 5
Update the Certificate Revocation List as described in First time a TGML graphic is opened after logging in it takes a long time for the graphic to load.