Issue
Can the existing communication wiring from a NETWORK 8000 (ASD) or DMS (Microsmart) project be re-used for a BACnet MS/TP trunk?
Environment
- NETWORK 8000 (ASD) cable
- DMS (MicroSmart) cable
- BACnet MS/TP
Cause
Using ASD cable become an issue as baud rates increases pass the range of 9600 or 19.2 k.
Resolution
Testing has shown that existing communication wiring of a NETWORK 8000 (ASD)or DMS (MicroSmart) system is compatible at a speed setting of 9600 baud. It is unlikely that this wire will work at higher baud rates or at extended distances. Communications will be limited to the slower baud rates (9600 or 19200 baud) on these systems.