Cameras can't be learned in Continuum except one

Cameras can't be learned in Continuum except one

Issue

When integrate with Pelco Endura system, after configure video serer in continuum correctly, there is only one camera can be found, the other cameras not come in.

Environment

Continuum 1.92~1.94

Endura 2.0

Cause

The cameras in Endura not be assigned a sequence number.

Resolution

  1. Ask Endura engineer to set a unique number to each camera
  2. Click "learn Camera" in Continuum video server editor

After the above steps done, all the cameras will come in Continuum if the connection in Endura side is correct.