Issue

Continuum has a limit on the number of entries that can be added to the BBMD table in the bCX and CyberStation.

Do the AS and ES servers have the same limitation?

Environment

  • Automation Server
  • Enterprise Server

Cause

Limitations must be known for engineering design.

Resolution

The number of BDT Entries you can add to the BBMD table in SmartStruxure is limited only by the available resources, so for all practical purpose there is no limit.

 

 

Device

BDT (Broadcast Distribution Table)

FDT (Foreign Device Table)

ES

only limited by memory

64

AS

only limited by memory

64

bCX1

32

32

Cyberstation

1024

1024