BAS2800+ - A BAS2800+ backup is not available for this site.

BAS2800+ - A BAS2800+ backup is not available for this site.

Issue

A site backup is not available.

Product Line

BAS2800+

Environment

  • BAS2800+
  • Backup
  • No Index
  • Uploading

Cause

The site is stand alone and the backup is not available.

Resolution

To recover the site data carry out the following;

  • Use the Pocket Terminal programme to review the outstation node configuration.
  • Setup the BAS2800+ terminal to match the configuration observed from the node.

Using the BAS2800+ System Diagnostics;

  • Select the outstation number and then from the options menu, select "Transfer Files"
  • Select to transfer PNTFLE.REC from the outstation, to C:\BAS\Data\osn??\PNTFLE.REC

Shutdown BAS2800+

Locate and run the "No Index" utility.

Run the utility to create the index

Restart BAS2800+ and confirm that the points are available and can be displayed.

Please note the "No Index" utility cannot name the index segments, this will need to be done by hand.

Link to download the No Index utility