Issue
The process of merging two Index files.
Environment
BAS 2800+
BasFiles
Merging
Indexes
Cause
BasFiles in it's basic form cannot be used to merge Index files. A switch is required.
Resolution
When starting BasFiles normally the options presented are as follows;
To merge two BAS site Index files together, BasFiles needs to be used in a different mode, this mode is not normally available, and a switch is required.
To start BasFiles in the mode that enables merging, carry out the following..
From the Windows "Start" button select the "Run" option.
Browse to where BasFiles is located and select it.
To BasFiles.exe add the extension "space"scs as follows - BasFiles.exe scs
When run a new menu option is now available.
Having selected the "Merge" option, you will be presented with the window below.
Note - The directory structure used must be present before merging takes place..