Issue
After manually changing all the COV increments in a Niagara R2 station, the COV increment values never update.
Environment
Niagara R2
Cause
The COV increment property is not fetched during a poll. To receive an update on this property use the Upload All command on the device object.
Resolution
Follow the steps below in WorkPlace Pro to perform an Upload All on the device object:
- Navigate to the workspace of the container where the BACnet device object exists.
- Right click the device object and select upload all.
For further information on COV increment refer to the Niagara R2 BACnet Integration Reference manual